AutomationDirect CLICK PLUS
Sep 23, 2025, 4:47 PM UTC
  • Vendor: AutomationDirect
  • Equipment: CLICK PLUS
  • Vulnerabilities: Cleartext Storage of Sensitive Information, Use of Hard-coded Cryptographic Key, Use of a Broken or Risky Cryptographic Algorithm, Predictable Seed in Pseudo-Random Number Generator, Improper Resource Shutdown or Release, Missing Authorization
Successful exploitation of these vulnerabilities disclose sensitive information, modify device settings, escalate privileges, or cause a denial-of-service condition on the affected device.
The following AutomationDirect products are affected:
  • CLICK PLUS C0-0x CPU firmware: Versions prior to v3.71
  • CLICK PLUS C0-1x CPU firmware: Versions prior to v3.71
  • CLICK PLUS C2-x CPU firmware: Versions prior to v3.71
3.2.1 Cleartext Storage of Sensitive Information CWE-312
Cleartext storage of sensitive information was discovered in Click Programming Software version v3.60. The vulnerability can be exploited by a local user with access to the file system, while an administrator session is active, to steal credentials stored in clear text.
CVE-2025-54855 has been assigned to this vulnerability. A CVSS v3.1 base score of 4.2 has been calculated; the CVSS vector string is (AV:L/AC:L/PR:H/UI:R/S:U/C:H/I:N/A:N).
A CVSS v4 score has also been calculated for CVE-2025-54855. A base score of 4.1 has been calculated; the CVSS vector string is (AV:L/AC:L/AT:P/PR:H/UI:P/VC:H/VI:N/VA:N/SC:N/SI:N/SA:N).
3.2.2 Use of Hard-coded Cryptographic Key CWE-321
The use of a hard-coded cryptographic key was discovered in firmware version 3.60 of the Click Plus PLC. The vulnerability relies on the fact that the software contains a hard-coded AES key used to protect the initial messages of a new KOPS session.
CVE-2025-58069 has been assigned to this vulnerability. A CVSS v3.1 base score of 5.3 has been calculated; the CVSS vector string is (AV:N/AC:L/PR:N/UI:N/S:U/C:L/I:N/A:N).
A CVSS v4 score has also been calculated for CVE-2025-58069. A base score of 6.9 has been calculated; the CVSS vector string is (AV:N/AC:L/AT:N/PR:N/UI:N/VC:L/VI:N/VA:N/SC:N/SI:N/SA:N).
3.2.3 Use of a Broken or Risky Cryptographic Algorithm CWE-327
The use of a broken or risky cryptographic algorithm was discovered in firmware version 3.60 of the Click Plus PLC. The vulnerability relies on the fact that the software uses an insecure implementation of the RSA encryption algorithm.
CVE-2025-59484 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.3 has been calculated; the CVSS vector string is (AV:N/AC:L/PR:N/UI:R/S:U/C:H/I:H/A:L).
A CVSS v4 score has also been calculated for CVE-2025-59484. A base score of 8.7 has been calculated; the CVSS vector string is (AV:N/AC:L/AT:N/PR:N/UI:P/VC:H/VI:H/VA:L/SC:N/SI:N/SA:N).
3.2.4 Predictable Seed in Pseudo-Random Number Generator CWE-337
A predictable seed in pseudo-random number generator vulnerability has been discovered in firmware version 3.60 of the Click Plus PLC. The vulnerability relies on the fact that the software implements a predictable seed for its pseudo-random number generator, which compromises the security of the generated private keys.
CVE-2025-55069 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.3 has been calculated; the CVSS vector string is (AV:N/AC:L/PR:N/UI:R/S:U/C:H/I:H/A:L).
A CVSS v4 score has also been calculated for CVE-2025-55069. A base score of 8.7 has been calculated; the CVSS vector string is (AV:N/AC:L/AT:N/PR:N/UI:P/VC:H/VI:H/VA:L/SC:N/SI:N/SA:N).
3.2.5 Improper Resource Shutdown or Release CWE-404
An improper resource shutdown or release vulnerability has been identified in the Click Plus C2-03CPU-2 device running firmware version 3.60. The vulnerability allows an unauthenticated attacker to perform a denial-of-service attack by exhausting all available device sessions of the Click Programming Software.
CVE-2025-58473 has been assigned to this vulnerability. A CVSS v3.1 base score of 5.9 has been calculated; the CVSS vector string is (AV:N/AC:H/PR:N/UI:N/S:U/C:N/I:N/A:H).
A CVSS v4 score has also been calculated for CVE-2025-58473. A base score of 8.2 has been calculated; the CVSS vector string is (AV:N/AC:H/AT:N/PR:N/UI:N/VC:N/VI:N/VA:H/SC:N/SI:N/SA:N).
3.2.6 Missing Authorization CWE-862
An authorization bypass vulnerability has been discovered in the Click Plus C2-03CPU2 device firmware version 3.60. Through the KOPR protocol utilized by the Remote PLC application, authenticated users with low-level access permissions can exploit this vulnerability to read and modify PLC variables beyond their intended authorization level.
CVE-2025-55038 has been assigned to this vulnerability. A CVSS v3.1 base score of 6.8 has been calculated; the CVSS vector string is (AV:N/AC:H/PR:L/UI:N/S:U/C:H/I:H/A:N).
A CVSS v4 score has also been calculated for CVE-2025-55038. A base score of 7.6 has been calculated; the CVSS vector string is (AV:N/AC:H/AT:N/PR:L/UI:N/VC:H/VI:H/VA:N/SC:N/SI:N/SA:N).
3.2.7 Improper Resource Shutdown or Release CWE-404
An improper resource shutdown or release vulnerability has been identified in the Click Plus C2-03CPU-2 device running firmware version 3.60. The vulnerability allows an unauthenticated attacker to perform a denial-of-service attack by exhausting all available device sessions in the Remote PLC application.
CVE-2025-57882 has been assigned to this vulnerability. A CVSS v3.1 base score of 5.9 has been calculated; the CVSS vector string is (AV:N/AC:H/PR:N/UI:N/S:U/C:N/I:N/A:H).
A CVSS v4 score has also been calculated for CVE-2025-57882. A base score of 8.2 has been calculated; the CVSS vector string is (AV:N/AC:H/AT:N/PR:N/UI:N/VC:N/VI:N/VA:H/SC:N/SI:N/SA:N).
Luca Borzacchiello and Diego Zaffaroni of Nozomi Networks reported these vulnerabilities to Automation Direct.
AutomationDirect recommends that users update CLICK PLUS and firmware to V3.80.
If the update cannot be applied right away, the following compensating controls are recommended until the upgrade can be performed:
  • Network Isolation – Disconnect the CLICK PLUS PLC from external networks (e.g., the internet or corporate LAN) to reduce exposure.
  • Secure Communications – Use only trusted, dedicated internal networks or air-gapped systems for device communication.
  • Access Control – Restrict both physical and logical access to authorized personnel only.
  • Application Whitelisting – Configure whitelisting so that only trusted, pre-approved applications are allowed to run. Block any unauthorized software.
  • Endpoint Protection – Use antivirus or EDR tools and configure host-based firewalls to block unauthorized access attempts.
  • Logging & Monitoring – Enable and regularly review system logs to detect suspicious or unauthorized activity.
  • Backup & Recovery – Maintain secure, tested backups of the PLC and its configurations to minimize downtime in case of an incident.
  • Ongoing Risk Assessment – Continuously evaluate risks associated with running outdated firmware and adjust compensating measures accordingly.
  • September 23, 2025: Initial Publication
This is a companion discussion topic for the original entry at https://www.cisa.gov/news-events/ics-advisories/icsa-25-266-01