- CVSS v3 9.8
- Vendor: Festo
- Equipment: Controller CECC-S,-LK,-D Family Firmware
- Vulnerabilities: Exposure of Resource to Wrong Sphere, Untrusted Pointer Dereference, NULL Pointer Dereference, Files or Directories Accessible to External Parties, Out-of-bounds Write, Improper Privilege Management, Incorrect Permission Assignment for Critical Resource, Buffer Copy without Checking Size of Input ('Classic Buffer Overflow'), Missing Release of Memory after Effective Lifetime, Improper Handling of Exceptional Conditions, Use of a Broken or Risky Cryptographic Algorithm, Weak Password Recovery Mechanism for Forgotten Password, Use of Password Hash With Insufficient Computational Effort, Improper Access Control, Allocation of Resources Without Limits or Throttling, Improper Input Validation, Buffer Over-read, Use of Insufficiently Random Values, Improper Limitation of a Pathname to a Restricted Directory ('Path Traversal'), Uncontrolled Recursion, Missing Encryption of Sensitive Data, Improper Restriction of Operations within the Bounds of a Memory Buffer
Successful exploitation of these vulnerabilities could allow an attacker to crash services, escalate privileges, bypass authentication, or gain unauthorized access to sensitive systems and data.
Festo reports that the following products are affected:
- Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-D (All versions): All versions
- Festo Firmware (R06 (11.10.2016) = 2.3.8.1) installed on Festo Hardware Controller CECC-LK (All versions): All versions
- Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-S (All versions): All versions
- Festo Firmware (R06 (11.10.2016) = 2.3.8.1) installed on Festo Hardware Controller CECC-S (All versions): All versions
3.2.1 EXPOSURE OF RESOURCE TO WRONG SPHERE CWE-668
A remote, authenticated attacker could utilize the control program of the CODESYS Control runtime system to use the vulnerability in order to read and modify the configuration file(s) of the affected products.
CVE-2022-22515 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.1 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:H/I:H/A:N).
3.2.2 UNTRUSTED POINTER DEREFERENCE CWE-822
An authenticated, remote attacker can gain access to a dereferenced pointer contained in a request. The accesses can subsequently lead to local overwriting of memory in the CmpTraceMgr, whereby the attacker can neither gain the values read internally nor control the values to be written. If invalid memory is accessed, this results in a crash.
CVE-2022-22514 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.1 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:L/A:H).
3.2.3 NULL POINTER DEREFERENCE CWE-476
An authenticated remote attacker can cause a null pointer dereference in the CmpSettings component of the affected CODESYS products which leads to a crash.
CVE-2022-22513 has been assigned to this vulnerability. A CVSS v3.1 base score of 6.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H).
3.2.4 FILES OR DIRECTORIES ACCESSIBLE TO EXTERNAL PARTIES CWE-552
In CODESYS V3 web server before 3.5.17.10, files or directories are accessible to External Parties.
CVE-2021-36763 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:N/A:N).
3.2.5 OUT-OF-BOUNDS WRITE CWE-787
CODESYS Control Runtime system before 3.5.17.10 has a Heap-based Buffer Overflow.
CVE-2021-33485 has been assigned to this vulnerability. A CVSS v3.1 base score of 9.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.6 OUT-OF-BOUNDS WRITE CWE-787
CODESYS V3 web server before 3.5.15.40, as used in CODESYS Control runtime systems, has a buffer overflow.
CVE-2020-10245 has been assigned to this vulnerability. A CVSS v3.1 base score of 9.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.7 INCORRECT PERMISSION ASSIGNMENT FOR CRITICAL RESOURCE CWE-732
An issue was discovered in 3S-Smart CODESYS V3 through 3.5.12.30. A user with low privileges can take full control over the runtime.
CVE-2019-9008 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:H/I:H/A:H).
3.2.8 BUFFER COPY WITHOUT CHECKING SIZE OF INPUT ('CLASSIC BUFFER OVERFLOW') CWE-120
CODESYS 3 web server before 3.5.15.20, as distributed with CODESYS Control runtime systems, has a Buffer Overflow.
CVE-2019-18858 has been assigned to this vulnerability. A CVSS v3.1 base score of 9.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.9 OUT-OF-BOUNDS WRITE CWE-787
CODESYS V3 web server, all versions prior to 3.5.14.10, allows an attacker to send specially crafted http or https requests which could cause a stack overflow and create a denial-of-service condition or allow remote code execution.
CVE-2019-13548 has been assigned to this vulnerability. A CVSS v3.1 base score of 9.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.10 NULL POINTER DEREFERENCE CWE-476
3S-Smart Software Solutions GmbH CODESYS V3 OPC UA Server, all versions 3.5.11.0 to 3.5.15.0, allows an attacker to send crafted requests from a trusted OPC UA client that cause a NULL pointer dereference, which may trigger a denial-of-service condition.
CVE-2019-13542 has been assigned to this vulnerability. A CVSS v3.1 base score of 6.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H).
3.2.11 MISSING RELEASE OF MEMORY AFTER EFFECTIVE LIFETIME CWE-401
CODESYS Control runtime system before 3.5.16.10 allows Uncontrolled Memory Allocation.
CVE-2020-15806 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.12 IMPROPER HANDLING OF EXCEPTIONAL CONDITIONS CWE-755
An issue was discovered in 3S-Smart CODESYS before 3.5.15.0 . Crafted network packets cause the Control Runtime to crash.
CVE-2019-9009 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.13 EXPOSURE OF RESOURCE TO WRONG SPHERE CWE-668
In Pilz PMC programming tool 3.x before 3.5.17 (based on CODESYS Development System), an attacker can identify valid usernames.
CVE-2019-9011 has been assigned to this vulnerability. A CVSS v3.1 base score of 5.3 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:L/I:N/A:N).
3.2.14 USE OF A BROKEN OR RISKY CRYPTOGRAPHIC ALGORITHM CWE-327
An issue was discovered in 3S-Smart CODESYS V3 products. The application may utilize non-TLS based encryption, which results in user credentials being insufficiently protected during transport. All variants of the following CODESYS V3 products in all versions containing the CmpUserMgr component are affected regardless of the CPU type or operating system: CODESYS Control for BeagleBone, CODESYS Control for emPC-A/iMX6, CODESYS Control for IOT2000, CODESYS Control for Linux, CODESYS Control for PFC100, CODESYS Control for PFC200, CODESYS Control for Raspberry Pi, CODESYS Control RTE V3, CODESYS Control RTE V3 (for Beckhoff CX), CODESYS Control Win V3 (also part of the CODESYS Development System setup), CODESYS V3 Simulation Runtime (part of the CODESYS Development System), CODESYS Control V3 Runtime System Toolkit, CODESYS HMI V3.
CVE-2019-9013 has been assigned to this vulnerability. A CVSS v3.1 base score of 8.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:A/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.15 WEAK PASSWORD RECOVERY MECHANISM FOR FORGOTTEN PASSWORD CWE-640
In Pilz PMC programming tool 3.x before 3.5.17 (based on CODESYS Development System), a user's password may be changed by an attacker without knowledge of the current password.
CVE-2020-12067 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:H/A:N).
3.2.16 USE OF PASSWORD HASH WITH INSUFFICIENT COMPUTATIONAL EFFORT CWE-916
In CODESYS V3 products in all versions prior V3.5.16.0 containing the CmpUserMgr, the CODESYS Control runtime system stores the online communication passwords using a weak hashing algorithm. This can be used by a local attacker with low privileges to gain full control of the device.
CVE-2020-12069 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.8 has been calculated; the CVSS vector string is (CVSS:3.1/AV:L/AC:L/PR:L/UI:N/S:U/C:H/I:H/A:H).
3.2.17 NULL POINTER DEREFERENCE CWE-476
In CODESYS Gateway V3 before 3.5.17.10, there is a NULL Pointer Dereference. Crafted communication requests may cause a Null pointer dereference in the affected CODESYS products and may result in a denial-of-service condition.
CVE-2021-36764 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.18 ALLOCATION OF RESOURCES WITHOUT LIMITS OR THROTTLING CWE-770
An issue was discovered in 3S-Smart CODESYS V3 products. A crafted communication request may cause uncontrolled memory allocations in the affected CODESYS products and may result in a denial-of-service condition. All variants of the following CODESYS V3 products in all versions prior to v3.5.14.20 that contain the CmpGateway component are affected, regardless of the CPU type or operating system: CODESYS Control for BeagleBone, CODESYS Control for emPC-A/iMX6, CODESYS Control for IOT2000, CODESYS Control for Linux, CODESYS Control for PFC100, CODESYS Control for PFC200, CODESYS Control for Raspberry Pi, CODESYS Control V3 Runtime System Toolkit, CODESYS Gateway V3, CODESYS V3 Development System.
CVE-2019-9012 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.19 ALLOCATION OF RESOURCES WITHOUT LIMITS OR THROTTLING CWE-770
CODESYS Control V3, Gateway V3, and HMI V3 before 3.5.15.30 allow uncontrolled memory allocation which can result in a remote denial of service condition.
CVE-2020-7052 has been assigned to this vulnerability. A CVSS v3.1 base score of 6.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:L/UI:N/S:U/C:N/I:N/A:H).
3.2.20 OUT-OF-BOUNDS WRITE CWE-787
An exploitable memory corruption vulnerability exists in the Name Service Client functionality of 3S-Smart Software Solutions CODESYS GatewayService. A specially crafted packet can cause a large memcpy, resulting in an access violation and termination of the process. An attacker can send a packet to a device running the GatewayService.exe to trigger this vulnerability. All variants of the CODESYS V3 products in all versions prior V3.5.16.10 containing the CmpRouter or CmpRouterEmbedded component are affected, regardless of the CPU type or operating system: CODESYS Control for BeagleBone, CODESYS Control for emPC-A/iMX6, CODESYS Control for IOT2000, CODESYS Control for Linux, CODESYS Control for PLCnext, CODESYS Control for PFC100, CODESYS Control for PFC200, CODESYS Control for Raspberry Pi, CODESYS Control RTE V3, CODESYS Control RTE V3 (for Beckhoff CX), CODESYS Control Win V3 (also part of the CODESYS Development System setup), CODESYS Control V3 Runtime System Toolkit, CODESYS V3 Embedded Target Visu Toolkit, CODESYS V3 Remote Target Visu Toolkit, CODESYS V3 Safety SIL2, CODESYS Edge Gateway V3, CODESYS Gateway V3, CODESYS HMI V3, CODESYS OPC Server V3, CODESYS PLCHandler SDK, CODESYS V3 Simulation Runtime (part of the CODESYS Development System).
CVE-2019-5105 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.21 NULL POINTER DEREFERENCE CWE-476
CODESYS Gateway 3 before 3.5.16.70 has a NULL pointer dereference that may result in a denial of service (DoS).
CVE-2021-29241 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.22 IMPROPER INPUT VALIDATION CWE-20
CODESYS Control Runtime system before 3.5.17.0 has improper input validation. Attackers can send crafted communication packets to change the router's addressing scheme and may re-route, add, remove or change low level communication packages.
CVE-2021-29242 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.3 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:L/I:L/A:L).
3.2.23 BUFFER OVER-READ CWE-126
A remote, unauthenticated attacker can send a specific crafted HTTP or HTTPS requests causing a buffer over-read resulting in a crash of the webserver of the CODESYS Control runtime system.
CVE-2022-22519 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.24 USE OF INSUFFICIENTLY RANDOM VALUES CWE-330
An unauthenticated, remote attacker can disrupt existing communication channels between CODESYS products by guessing a valid channel ID and injecting packets. This results in the communication channel to be closed.
CVE-2022-22517 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:N/A:H).
3.2.25 IMPROPER LIMITATION OF A PATHNAME TO A RESTRICTED DIRECTORY ('PATH TRAVERSAL') CWE-22
CODESYS V3 web server, all versions prior to 3.5.14.10, allows an attacker to send specially crafted http or https requests which may allow access to files outside the restricted working directory of the controller.
CVE-2019-13532 has been assigned to this vulnerability. A CVSS v3.1 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.1/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:N/A:N).
3.2.26 USE OF INSUFFICIENTLY RANDOM VALUES CWE-330
Use of Insufficiently Random Values exists in CODESYS V3 products versions prior V3.5.14.0.
CVE-2018-20025 has been assigned to this vulnerability. A CVSS v3.0 base score of 7.5 has been calculated; the CVSS vector string is (CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:N/A:N).
3.2.27 UNCONTROLLED RECURSION CWE-674
Constructed ASN.1 types with a recursive definition (such as can be found in PKCS7) could eventually exceed the stack given malicious input with excessive recursion. This could result in a Denial Of Service attack. There are no such structures used within SSL/TLS that come from untrusted sources so this is considered safe. Fixed in OpenSSL 1.1.0h (Affected 1.1.0-1.1.0g). Fixed in OpenSSL 1.0.2o (Affected 1.0.2b-1.0.2n).
CVE-2018-0739 has been assigned to this vulnerability. A CVSS v3.0 base score of 6.5 has been calculated; the CVSS vector string is (CVSS:3.0/AV:N/AC:L/PR:N/UI:R/S:U/C:N/I:N/A:H).
3.2.28 MISSING ENCRYPTION OF SENSITIVE DATA CWE-311
In 3S-Smart Software Solutions GmbH CODESYS Control V3 products prior to version 3.5.14.0, user access management and communication encryption is not enabled by default, which could allow an attacker access to the device and sensitive information, including user credentials.
CVE-2018-10612 has been assigned to this vulnerability. A CVSS v3.0 base score of 9.8 has been calculated; the CVSS vector string is (CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:H/I:H/A:H).
3.2.29 IMPROPER RESTRICTION OF OPERATIONS WITHIN THE BOUNDS OF A MEMORY BUFFER CWE-119
While parsing an IPAddressFamily extension in an X.509 certificate, it is possible to do a one-byte overread. This would result in an incorrect text display of the certificate. This bug has been present since 2006 and is present in all versions of OpenSSL before 1.0.2m and 1.1.0g.
CVE-2017-3735 has been assigned to this vulnerability. A CVSS v3.0 base score of 5.3 has been calculated; the CVSS vector string is (CVSS:3.0/AV:N/AC:L/PR:N/UI:N/S:U/C:N/I:L/A:N).
CERT@VDE coordinated and supported publication with Festo. Festo reported these vunerabilities to CISA.
Festo has identified the following specific workarounds and mitigations users can apply to reduce risk:
- (CVE-2022-22515, CVE-2022-22514, CVE-2022-22513, CVE-2021-36763, CVE-2021-33485, CVE-2020-10245, CVE-2020-15806, CVE-2019-9011, CVE-2019-9013, CVE-2020-12067, CVE-2020-12069, CVE-2021-36764, CVE-2019-5105, CVE-2021-29241, CVE-2021-29242, CVE-2022-22519, CVE-2022-22517, CVE-2018-0739) (Product Group: Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-D(All versions), Festo Firmware (R06 (11.10.2016) = 2.3.8.1) installed on Festo Hardware Controller CECC-LK(All versions), Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-S(All versions)): No fix planned. This issue will be handled with next hardware generation release.
- (CVE-2019-9008, CVE-2019-18858, CVE-2019-13548, CVE-2019-13542, CVE-2019-9009, CVE-2019-9012, CVE-2020-7052, CVE-2019-13532, CVE-2018-20025, CVE-2018-10612, CVE-2017-3735) (Product Group: Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-D(All versions), Festo Firmware (R06 (11.10.2016) = 2.3.8.1) installed on Festo Hardware Controller CECC-LK(All versions), Festo Firmware (R05 (17.06.2016) = 2.3.8.0) installed on Festo Hardware Controller CECC-S(All versions)): Update to version 2.4.2.0. This also fixes CODESYS Advisory 2017-01, CODESYS Advisory 2017-03, CODESYS Advisory 2017-06, CODESYS Advisory 2017-07, CODESYS Advisory 2017-09, CODESYS Advisory 2018-04, CODESYS Advisory 2018-05, CODESYS Advisory 2018-07, CODESYS Advisory 2018-11.
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-9008
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-9008
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-18858
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-18858
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-13548
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-13548
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-13542
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-13542
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-9009
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-9009
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-9012
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-9012
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2020-7052
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2020-7052
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2019-13532
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2019-13532
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2018-20025
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2018-20025
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2018-0739
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2018-0739
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2018-10612
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2018-10612
- Firmware 2.4.2.0 installed on Controller CECC-D are fixed versions for CVE-2017-3735
- Firmware 2.4.2.0 installed on Controller CECC-LK are fixed versions for CVE-2017-3735
For more information see the associated Festo SE & Co. KG security advisory FSA-202202 FSA-202202: Festo: Controller CECC-S,LK,D family <= 2.3.8.1 - multiple vulnerabilities in CODESYS V3 runtime system - HTML, FSA-202202: Festo: Controller CECC-S,LK,D family <= 2.3.8.1 - multiple vulnerabilities in CODESYS V3 runtime system - CSAF.
- September 30, 2025: Initial Republication of Festo FSA-202202
This is a companion discussion topic for the original entry at https://www.cisa.gov/news-events/ics-advisories/icsa-25-273-04